I'm curious as to how you would supply a 120 volt receptacle from say a 2P-40 amp feeder for a roof top unit?I believe the code requres gfi or wp/gfi with in 25 feet of a roof top unit. In this office we spec a 120V gfi with the unit, wired on the supply side of the disconnect
I guess that an xfmr would work. We always just run 2-#12 conductors up to the roof for the receptacle. This seems simpler than getting involved with transformers and overcurrent protection devices.a small xfmr tapped off the line side of the feeder before the disconnect?
That's true, but are you going to run a 120V line at let's say 100 feet to every unit? The transformer might be much cheaper with wiring cost.Originally posted by infinity:
I guess that an xfmr would work. We always just run 2-#12 conductors up to the roof for the receptacle. This seems simpler than getting involved with transformers and overcurrent protection devices.a small xfmr tapped off the line side of the feeder before the disconnect?
Well depending on the placement of the units I would only need a receptacle within 25' so one receptacle may serve several units. A transformer would require a 3R enclosure and overcurrent protection and I would still need to install a receptacle in a box etc. I'd guess that this type of installation would be very subjective. Sometimes the XFMR would be better, sometimes not.That's true, but are you going to run a 120V line at let's say 100 feet to every unit? The transformer might be much cheaper with wiring cost
I know we spec a weatherproof gfi receptacle, but as far as the "while in use cover", not on our end. We ask the mechanicals to add a GFCI receptacle speced with the unit. This receptacle is completely prewired, so in essence, all we have to do is show up with the 480V, 240V, or 208V. When it is spec with the unit, is a heck of a lot cheaper than running a 120V line to all the units, because it's factory installed. JMO!Originally posted by sceepe:
Do you guys think that the hvac receptacle requires a while in use cover as per 406.8. Roof top is a wet location. You doing this lady?
did not suggest it was a good idea. just an oversite in the code requirements.Originally posted by marissa2:
How long do you think that 5 amp fuse would last when the HVAC tech plugs in his vacuum pump.
Lou
I agree with your logic but 406.8 does not leave any room for logic.I don't think it needs an in use cover. thats appropriate where the outlet is used continuously, but this outlet is just there for the service guy's use a few hours a year.
the handboook goes on to say that,(1) 15- and 20- Ampere Receptacles in a Wet Location
15- and 20-ampere, 125- and 250-volt receptacles installed in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted.
The requirement for this type of cover is not contingent on the anticipated use of the receptacle.
That's why it's on the line side, with a transformer already factory installed. If the disconnect is off the receptacle fed from the line side remainse on still.Originally posted by bwyllie:
we have the receptacle installed on its own 120V circuit because if the unit's disconnect is off for repairs the receptacle supplied with the unit is also off.