N nizak Senior Member Dec 8, 2010 #1 Would anyone here know what the load of a 20 ton roof top A/C GFA unit would be 208/230V 3Ph? Even an approximation would be helpful.Thanks.
Would anyone here know what the load of a 20 ton roof top A/C GFA unit would be 208/230V 3Ph? Even an approximation would be helpful.Thanks.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Dec 8, 2010 #2 Approximation: 1kva per ton. No nameplate specs?
T topgone Senior Member Dec 9, 2010 #3 nizak said: Would anyone here know what the load of a 20 ton roof top A/C GFA unit would be 208/230V 3Ph? Even an approximation would be helpful.Thanks. Click to expand... 1 ton of refrigeration = 12,000 BTU (heat) Power input = AC load(heat)/SEER (seasonal energy efficiency ratio) Assume SEER = 10 BTU(heat)/watt(electric): Power input = 20 x 12,000BTU/10 = 24,,000 watts in kVA, assume: PF = 0.8; Pin = 24 kW/0.8 so Pin = 30 kVA kVA/ton = 30/20 = 1.5 kVA per ton With higher energy efficiency ratios (depending on the heat pump) and higher efficiency motors, you could use 1 kVA per ton as Larry said. Still, it's best to refer to OEM datasheets.
nizak said: Would anyone here know what the load of a 20 ton roof top A/C GFA unit would be 208/230V 3Ph? Even an approximation would be helpful.Thanks. Click to expand... 1 ton of refrigeration = 12,000 BTU (heat) Power input = AC load(heat)/SEER (seasonal energy efficiency ratio) Assume SEER = 10 BTU(heat)/watt(electric): Power input = 20 x 12,000BTU/10 = 24,,000 watts in kVA, assume: PF = 0.8; Pin = 24 kW/0.8 so Pin = 30 kVA kVA/ton = 30/20 = 1.5 kVA per ton With higher energy efficiency ratios (depending on the heat pump) and higher efficiency motors, you could use 1 kVA per ton as Larry said. Still, it's best to refer to OEM datasheets.