What's the minimum height conduit can be installed on a commercial roof?
What's the minimum height conduit can be installed on a commercial roof?
Rigid can be walked on.
If your talking flat roof I usually screw the conduit to cement or treated lumber blocks to keep it up off the surface a bit and give it some weight.... that's about it.
I don't want to be in anyway responsible for penetrating a rubber roof.
If you are under the 2014 code and you use XHHW conductors, you don't have to add the additional temperature required by 310.15(B)(3)(c).
If you are under the 2014 code and you use XHHW conductors, you don't have to add the additional temperature required by 310.15(B)(3)(c).
Testing was done by UL and General Cable that proved that the XHHW does not degrade with heat like THHN?THWN does.I don't yet have 2014, but any idea why?
Testing was done by UL and General Cable that proved that the XHHW does not degrade with heat like THHN?THWN does.
ooh. i didn't know that.... so i want to pull xhhw conductors on roofs then?
good to know... thank you. i have 3 package units coming up shortly.
I think that may be next. However other wire manufacturers tried to prevent this change from getting into the code. There was extensive floor debate on this change at the NFPA meeting where the code was adopted by the membership. The comments in opposition said that there are a number of different formulations of XHHW-2 and that they were not all tested for use at higher temperatures. (of course the more copper the more profit for the wire manufacturer)That is fine, but if it can take more heat why doesn't it have more than 90C rating :?..
True, but if you are the one that has the higher rating and can use less copper, guess who sells more in the end:happyyes:(of course the more copper the more profit for the wire manufacturer)
But the code rule applies to all XHHW-2 no matter who makes it. The objectors did not want the higher rating to apply to any conductor.True, but if you are the one that has the higher rating and can use less copper, guess who sells more in the end:happyyes:
Well my comment applies to what makes most sense and not what the greedy copper thieves, I mean suppliers, wantBut the code rule applies to all XHHW-2 no matter who makes it. The objectors did not want the higher rating to apply to any conductor.
But where do we stop? Next people will want to use XHHW in other high temperature applications. Besides we went for many years without the ambient temp adder even though rooftops are brutal environments temperature wise, then we finally came up with a method to deal with that environment, but now we are going to turn back a little and say it doesn't matter again?Part of the Code change issue may just be that it is easier to drop the ambient temperature adder than to include new tables for higher voltage insulation. And of course the terminations will still be a limiting factor for the whole wire run even if they are not on the roof area.