Rooftop AC lighting and receptacle requirements

Status
Not open for further replies.

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
An EC friend of mine is on a project where they are replacing rooftop AC units. he asked me if a light and GFCI receptacle required for these replacements ? I looked in Article 440 but did not notice a requirement.
 

Kansas Mountain

Senior Member
Location
Oklahoma, United States
Occupation
Lighting and Lighting Control Designs
Maintenance receptacles are required at the same level and within 25' of all HVACR equipment. All of your rooftop units don't necessarily require their own maintenance receptacle, a single receptacle can cover multiple units if they are within range of multiple units. Ref 210.63.

Never heard of a lighting requirement that would apply.
 

jap

Senior Member
Occupation
Electrician
I think he's questioning the fact that now that they are changing the unit out whether or not they need to add one.

JAP>
 

Ken_S

Senior Member
Location
NJ
Occupation
Electrician
If this is in NJ and considered a renovation, then the provisions of the rehab subcode should apply and would exempt the required receptacles. See 5:23-6.8 (d)
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
I worked on a site where there was a spec that called for a light and recpt. This was a mall project which could be serviced at night. It was a first for me. The GC supplied the light. It was a vapor tight fixture with guard.
I'm not aware if it is an NEC requirement for a light.
We had recpt then FS switch and then the light all in an imc Assembly.
 

Attachments

  • Screenshot_20220920-193143.png
    Screenshot_20220920-193143.png
    246.9 KB · Views: 2

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
I think he's questioning the fact that now that they are changing the unit out whether or not they need to add one.

JAP>
Yes, that was the intent of my post but also wanted to know if it was ever an NEC requirement. Thanks.
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
If this is in NJ and considered a renovation, then the provisions of the rehab subcode should apply and would exempt the required receptacles. See 5:23-6.8 (d)
Yes, it is in NJ. My friend came back to me and said that he thought that some time ago it was a PSE&G requirement if the unit had gas and was also used for heating. I have no documentation to back that up. Thanks for your reply.
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
I worked on a site where there was a spec that called for a light and recpt. This was a mall project which could be serviced at night. It was a first for me. The GC supplied the light. It was a vapor tight fixture with guard.
I'm not aware if it is an NEC requirement for a light.
We had recpt then FS switch and then the light all in an imc Assembly.
I've seen that set-up in many locations. I never thought about it being an NEC requirement but rather a design spec.
 

raberding

Senior Member
Location
Dayton, OH
Occupation
Consulting Engineer
I recall that at one time a light at RTUS was a Mechanical Code requirement. Now I gotta do some research...
 