Is it ok to come off the bottom of disconnect with an 1/2 inch offset nipple to a bell box for the service GFCI ?
Is it ok to come off the bottom of disconnect with an 1/2 inch offset nipple to a bell box for the service GFCI ?
Thanks Kwired, Yes I have a separate 120 volt circuit, what I was wondering is coming off the bottom of disconnect with offset nipple OK, If water would be an issue or not.
210.23(A)(2) Utilization Equipment Fastened in Place. The total rating
of utilization equipment fastened in place, other than luminaires,
shall not exceed 50 percent of the branch-circuit ampere
rating where lighting units, cord-and-plug-connected utilization
equipment not fastened in place, or both, are also supplied.
Dennis, I do have a 120V circuit with a neutral, Are you thinking someone might get a hot from the disconnect and use the egc for a neutral.
Dennis, I do have a 120V circuit with a neutral, Are you thinking someone might get a hot from the disconnect and use the egc for a neutral.
Drill the weep hole and move on. Any thing else you do is a waste of time. Bottom line is if any sealing effort fails you still potentially fill/partially fill the box with water. Even well sealed box can still fill with condensation.If using a bell box, drill a small hole in the bottom to let the water out. I would always use SS screws on recpt and cover but the WR recpts have SS screws.
duct seal on the inside over any threaded KO plugs, think the instructions mention this. I would silicone between the inuse cover and box
You also need to watch for this.
Also you need a neutral in the box also
Yes, but the fixed load (the AC) must be 10 amps or less to be able to place the receptacle on the same circuit.Let us say the AC unit needs 20 amps 240 volts. Would it be permissible to simply run a neutral with the two hot conductors to supply the GFCI with 120 volts?