As you know, for sizing general conductors, one must consider ambient temperature and conductor bundling. When the conductors are installed in a rooftop, and their bottom are 2.3 cm or less from the rooftop, then one must add 33°C to the estimated ambient temperature, as per sec. 310.15(B)(2) of the 2020 NEC. So if the ambient temperature was 40°C, it would become 73°C.
On the other hand, when one is sizing conductors for PV circuits, instead of using the ambient temperature correction factors for general wiring (table 310.15(B)(1)), the NEC allows to use that in the article dedicated to PV systems (table 690.31(A)(a)).
My question is, if I'm sizing the PV wires, which will be installed in a rooftop and less than 2.3 cm, must I still add the 33°C required by sec. 310.15(B)(2) when using table 690.31(A)(a)?
On the other hand, when one is sizing conductors for PV circuits, instead of using the ambient temperature correction factors for general wiring (table 310.15(B)(1)), the NEC allows to use that in the article dedicated to PV systems (table 690.31(A)(a)).
My question is, if I'm sizing the PV wires, which will be installed in a rooftop and less than 2.3 cm, must I still add the 33°C required by sec. 310.15(B)(2) when using table 690.31(A)(a)?