Sparky1981
PE
- Location
- Denver, CO
- Occupation
- Electrical/Lighting Engineer
I have an RTU unit that calls for MOCP 70A. This is an existing building. After 30 day metering a few panels we do not have capacity in any of them for this unit. Our only option is the old Westinghouse service gear. Not easy to get parts for. There is an existing 800A breaker that we can put a 400A digitrip unit in. Lowest we could find. What I am proposing is a 400A feeder from that breaker in the main gear to a 200A fused disconnect that has 70A fuses in it. As close to the gear as possible to limit the 400A feeder. Then do a 70A feeder from the fused disconnect to the unit. Anybody see any issues? I dont think this is a tap because the 400A feeder is protected.
