When replaceing rooftop units is it required to install new disconnects even if old ones are working properly .There are outlets within the 25 foot requirement.
The only reason we are questioning it is this is what the inspector wants.The disconnects are good with all proper labels on them.Never had to change out old disconnects if they are funcitional.They are 600 volt and not cheap.Which code cycle are you under? Is the disconnect fused or nonfused? The only thing I could think of you needing to change it out would be based upon an updated available fault current calculation condition at the unit, and if the fused/nonfused disconnect has a sufficient short circuit current rating at it; this could occur if the utility has upgraded to a larger transformer, or other site conditions that are only speculative at this point.
Are there specifications to change it as well? Heavy Duty versus General Duty and whether or not specifications call for a certain type.
The only reason we are questioning it is this is what the inspector wants.The disconnects are good with all proper labels on them.Never had to change out old disconnects if they are funcitional.They are 600 volt and not cheap.