Hi all, sorry for the long post but I want to give you all the relevant details.
I am working with a local ISP to install an outdoor wireless internetaccess point. I have some questions about grounding and lighting protection. We are in an area that gets a few severe thunderstorms every year.
All the electrical service and telephone / data lines enter the building (an older wood frame house) in the same area, just above ground level on the north wall. The electric meter, service panel and telephone network interfaces are all bonded to either the conduit that enters the electric meter, or to the conduit that enters the building from the service panel. The service panel is apparently connected to one or more ground rods (can't see, but a large bare wire goes through a small PVC conduit to the ground) and to the water pipe on the other side of the basement.
The access point electronics and antenna are mounted on a tripod located atop the center of the roof. The antenna is on a 10' steel mast. The access point is inside a fiberglass NEMA 4 enclosure. The antenna lead goes through a PolyPhaser filter protector mounted on the enclosure. Power and data will come in over CAT 5 cable.
There is a swamp cooler nearby, with power run through metal conduit and a sheet metal cone and flashing over a hole in the roof. The conduit goes through the cone unbroken.
I would like to connect the tripod base, coax ground and a CAT 5 surge protector to the ground lug on the NEMA enclosure. Then run the ground wire and the CAT5 cable through flexible plastic conduit to the existing sheet metal cone under the swamp cooler. Inside the attic I would install another CAT 5 surge protector, and run the ground wire through the attic to the wall with the service entrance, then bond it to the service entrance conduit.
My concerns are for equipment safety and performance, as well as code compliance. I have read section 820 of the NEC, but I'm not sure that I understand all the implications.
Is this plan reasonable, safe and in code? If not, what do you suggest.
Thanks in advance for your help.
Reed.
I am working with a local ISP to install an outdoor wireless internetaccess point. I have some questions about grounding and lighting protection. We are in an area that gets a few severe thunderstorms every year.
All the electrical service and telephone / data lines enter the building (an older wood frame house) in the same area, just above ground level on the north wall. The electric meter, service panel and telephone network interfaces are all bonded to either the conduit that enters the electric meter, or to the conduit that enters the building from the service panel. The service panel is apparently connected to one or more ground rods (can't see, but a large bare wire goes through a small PVC conduit to the ground) and to the water pipe on the other side of the basement.
The access point electronics and antenna are mounted on a tripod located atop the center of the roof. The antenna is on a 10' steel mast. The access point is inside a fiberglass NEMA 4 enclosure. The antenna lead goes through a PolyPhaser filter protector mounted on the enclosure. Power and data will come in over CAT 5 cable.
There is a swamp cooler nearby, with power run through metal conduit and a sheet metal cone and flashing over a hole in the roof. The conduit goes through the cone unbroken.
I would like to connect the tripod base, coax ground and a CAT 5 surge protector to the ground lug on the NEMA enclosure. Then run the ground wire and the CAT5 cable through flexible plastic conduit to the existing sheet metal cone under the swamp cooler. Inside the attic I would install another CAT 5 surge protector, and run the ground wire through the attic to the wall with the service entrance, then bond it to the service entrance conduit.
My concerns are for equipment safety and performance, as well as code compliance. I have read section 820 of the NEC, but I'm not sure that I understand all the implications.
Is this plan reasonable, safe and in code? If not, what do you suggest.
Thanks in advance for your help.
Reed.