 Is there a required height for stand wall outlet 120 volt 15/20 amp residential and\or commerical in the electrical code? If so where? If not is there a industry standard? What is the reference?
 Thank you
 
 IP: 12.23.221.66
  
 Member 
    
 Name: Len Bonosevich
 Email: 
lennyelias@earthlink.net
 Location: New hampshire
 Title: Electrician
 In Trade Since: 1976
 Registered: Jan 2003
 Total Posts: 185
   posted February 13, 2003 at 10:01 AM         
 --------------------------------------------------------------------------------
 No, but,
 Typically 44 - 46" to bottom of switch boxes.
 10 - 14" to bottom of recepts except in gararges where 18" to bottom of box is "trade standard"(based on mechanical code requiring heating systems to be elevated due to gas fumes). Many prefer 52" in garage (over height of sheet goods laying against wall)
 
 There is NEC requirement for countertops - not to exceed 18" above countertop. I think you can find it under required receptacles in Art 210
 
 Check out ADA, Americans with Disablities Act for HUD multifamily etc.
 
 see this thread: 
http://electrical-contractor.net/ubb/Forum1/HTML/002500.html 
 
 Len
 
 
 IP: 209.245.101.236
  
 Member 
    
 Name: David Newton
 Email: 
dana1028@yahoo.com
 Location: California
 Title: Electrician, Inspector
 In Trade Since: 1985
 Registered: Jul 2001
 Total Posts: 157
   posted February 13, 2003 at 12:57 PM         
 --------------------------------------------------------------------------------
 ADA (Americans with Disabilities Act) does have requirements for recep/switch heights - see copy of a previous thread below:
 Receptacle Mounting Height
 
 Question: Mike, I am an apprentice electrician and I was told that the 1999 NEC requires wall-mounted receptacles for commercial buildings to be mounted so that the bottom of the cover plate is no less than 15 inches from the floor. Is this True?
 Mike Answer: No. There is no NEC requirement on the height of wall-mounted receptacles in residential, commercial, or industrial facilities, but?.
 
 American Disabilities Act Requirement
 
 The Code of Federal Regulations 28 Part 36 (American Disabilities Act) in Section 4.27.3 states that electrical and communications system receptacles on walls shall be mounted no less than 15" above floor. However, the exception indicates that this does not apply to receptacles not intended for use by building occupants. The maximum height for receptacles and/or switches is between 48 and 54 inches, depending on the conditions, see Section 4.2.5 and 4.2.6 of the ADA. 
 From: Tracey Leach-Casey 
tleach@swinerton.com <mailto:tleach@swinerton.com>
 
 
 Building Codes
 
 The N.E.C may not have requirements for receptacle heights, but if the jurisdiction you are working in enforces CABO/ANSI A117.1 1992 for Accessibility, Section 4.25.3 (exception) states: Electrical and communication system receptacles on walls shall be mounted 15 inches above the floor unless the use of special equipment requires location at a different position. The ANSI standard is referenced in the 1997 U.B.C section 1101.3. 
 From: Gilbert Gonzales
 
 Regarding the question on the 15" receptacle height: The Uniform Building Code 1106.3.3 on Accessibility for the handicapped uses 15" to 48" for operating control heights within Section 1106 dealing with lighting controls, electrical receptacles, environmental controls, security and intercom 
 systems. You would have to read UBC 1103 to see if your occupancy type applies, but it generally covers commercial structures.
 From: 
Sarg763@aol.com <mailto:Sarg763@aol.com>
 
 
 If you have any additional comments, let me know 