[FONT="]Log#2253 6- 110 - (Tables 310-16 through 310-31, Note 8(c)-(New)): Accept in Principle [/FONT]
[FONT="] Secretary's Note: It was the action of the Correlating Committee that this proposal be reconsidered and correlated with the action on Proposals 6-58 and 6-105. This action will be considered by the Panel as a Public Comment. [/FONT]
[FONT="] The Correlating Committee agrees with Durham's comment. In addition the requirement is inappropriate in Note 8 because only derating for the number of conductors in a raceway is covered by the rule. SUBMITTER:[/FONT][FONT="] J. [/FONT][FONT="]W. Frasure, Houston, TX [/FONT]
[FONT="] RECOMMENDATION: Add new Note 8(c) as follows: [/FONT]
[FONT="] (c) Underground Raceway Exit Ampacities. Ampacity derating factors shall not be applied to underground conductors entering or leaving an underground direct burial trench or duct bank if such conductors have physical protection in the form of conduit, equipment cubicle, or other similar enclosure and the conductors do not have a length in excess of 10 feet. SUBSTANTIATION: In the application described above, the underground portion of the circuit acts as a heat sink and dissipates any small amount of extra heating that occurs in the aboveground portion of the circuit. Industrial applications have used 15 feet for these conditions for many years without problems. [/FONT]
[FONT="] This note permits terminating underground circuits in switchgear, terminal boxes, metering enclosures, etc. without derating. [/FONT]
[FONT="] PANEL ACTION: Accept in Principle. [/FONT]
[FONT="] Revise the proposal as follows and identify it as a new Note 8(c): [/FONT]
[FONT="] "8(c) Underground Exit Ampacities. Ambient temperature adjustment factors shall not be required for underground conductors entering or leaving an underground direct burial trench or duct bank if such conductors have a length of not more than 15 feet above grade. " [/FONT]
[FONT="] PANEL COMMENT: The Panel believes the revised wording more accurately reflects the intent of the proposal, eliminates the restrictions of raceways or enclosures and correlates with changes Panel accepted in Proposal 6-105.[/FONT]
[FONT="] VOTE ON PANEL ACTION: [/FONT]
[FONT="] AFFIRMATIVE: 9[/FONT]
[FONT="] NEGATIVE: Durham. [/FONT]
[FONT="] EXPLANATION OF VOTE: [/FONT]
[FONT="] DURHAM: Proposal-is inconsistent with action taken on Proposals 6-58 and 6-105. [/FONT]
[FONT="] COMMENT ON VOTE: [/FONT]
[FONT="] BROWN: I agree with Mr. Durham's negative vote comment. I am not changing my vote because I also agree with the panel's action on this proposal. I feel that we should correlate our actions on proposals 6-58 and 6-105 to agree with our action on this proposal. [/FONT]