I am wiring a rotary phase converter. Its a Kay Industries unit model MA-4-A-VS-PA3-20-S. The RPC supplies power to 3 rooftop HVAC units. I have a few questions. The unit nameplate lists ONLY the following information:
input single phase voltage-230v
output 3 phase voltage- 230v
HP-20
Largest motor-20
Unit does NOT list single phase FLA, but there is a spot for it on the nameplate. However, it is blank.
1- I am guessing that because the FLA is not listed on the RPC, I need to size the conductors to 250% of FLA of the 3 rooftop units. They only have a max rated amps on the nameplate. I am assuming this would be used as FLA. Would this be correct? I am planning on contacting Kay Industries regarding the FLA but I'm guessing there was a reason it was left blank in that area on the nameplate. I would rather size based on 125% FLA as it should upsize the conductors.
2- The RPC load side feeds a main lug panel adjacent to the RPC. This MLO panel in turn feeds the three units. Is any OCP required between the RPC and the MLO panel? It seems that the OCP provided on the single phase line side of the unit should protect the load side of the RPC based on the total KVA. Am I correct in assuming this?
I appreciate any feedback/advice.
input single phase voltage-230v
output 3 phase voltage- 230v
HP-20
Largest motor-20
Unit does NOT list single phase FLA, but there is a spot for it on the nameplate. However, it is blank.
1- I am guessing that because the FLA is not listed on the RPC, I need to size the conductors to 250% of FLA of the 3 rooftop units. They only have a max rated amps on the nameplate. I am assuming this would be used as FLA. Would this be correct? I am planning on contacting Kay Industries regarding the FLA but I'm guessing there was a reason it was left blank in that area on the nameplate. I would rather size based on 125% FLA as it should upsize the conductors.
2- The RPC load side feeds a main lug panel adjacent to the RPC. This MLO panel in turn feeds the three units. Is any OCP required between the RPC and the MLO panel? It seems that the OCP provided on the single phase line side of the unit should protect the load side of the RPC based on the total KVA. Am I correct in assuming this?
I appreciate any feedback/advice.