Something I never really put much thought to before. I have a router that I am being asked to supply power to. The cut-sheet simply says that the unit requires 40A input, but the unit can accept an input voltage of 100-240VAC. With this being a single phase unit would it be safe to surmise that the 40A rating is with 100VAC supply?
I am planning on supplyiung the unit with 208VAC if the 40A input is at 208VAC = 8.32 kVA, then I would be required to upsize the UPS supplying this unit.
Can I assume the requirement is 40A * 100VAC = 4.0 kVA? Therefore my load at 208VAC would only be 19.23A (4.0 kVA / 208VAC)?
Thanks for any input.