Is it code-compliant (please state code section if you have the answer) to run a #6 AWG grounding electrode conductor (gec) under the soil the required 6 feet from ground rod to ground rod then back into the residence to house panel? And if so, how deep must the conductor be placed (again please state code section)?
Section 250.64 states "where exposed, a gec shall be securely fastened to the surface upon which it is carried."
As AHJ, I inspected a service change where the homeowner was unhappy that the electrical contractor ran the bare copper #6 AWG gec on top of the ground between rods. But before I call the contractor back out, I would like to know if it is allowed that the gec can in fact be run in the ground between rods and at what depth.
Also the upper end of the ground rod and clamp are above ground by three inches. (I know that 8 feet of the electrode shall be installed in contact with the ground.) If honestly the contractor can't beat the rod further into the earth, does Section 250.53 (G), which allows the upper end of the rod to be protected against physical damage as specified in 250.10, allow the contractor to simply enclose the upper end of the rod, and if so, enclose it with what?
Thanks
Section 250.64 states "where exposed, a gec shall be securely fastened to the surface upon which it is carried."
As AHJ, I inspected a service change where the homeowner was unhappy that the electrical contractor ran the bare copper #6 AWG gec on top of the ground between rods. But before I call the contractor back out, I would like to know if it is allowed that the gec can in fact be run in the ground between rods and at what depth.
Also the upper end of the ground rod and clamp are above ground by three inches. (I know that 8 feet of the electrode shall be installed in contact with the ground.) If honestly the contractor can't beat the rod further into the earth, does Section 250.53 (G), which allows the upper end of the rod to be protected against physical damage as specified in 250.10, allow the contractor to simply enclose the upper end of the rod, and if so, enclose it with what?
Thanks