Originally posted by pierre:
Bob
As I have never had the experience of that type of installation, would you mind elaborating on that a little more?
Thanks
Pierre
I am guessing you mean the MI part of my post as I was only kidding about cutting a slot in a chase nipple.
I have only terminated MI cable a couple of times, the company I work for does it fairly regularly.
Type MI cable for those that have not seen it looks like soft drawn copper water pipe on the outside, there is no rubber or plastic insulation on the outside.(At least the kinds I have seen)
The outer cover is copper, inside that is a copper conductor insulated from the outer sheath by a white material that resembles gypsum. I do not really know what it is.
In smaller sizes it is multi conductor cable, in the larger sizes it is single conductor.
The single conductor MI cable is what we run so for a 3 phase 4 wire feeder you will have 4 of these conductors, the outside sheath being the grounding conductor.
Once you get to a panel we will as I said cut out a rectangle about 4" x 8" or 10" from the panel enclosure and bolt on a brass plate that covers this hole and is about 3/4" thick.
This brass plate has holes threaded in it that receive the MI connectors that look much like brass compression plumbing fittings.
The use of this brass piece being non-ferris keeps us from having heating problems from passing the single conductors through the steel panel tub.
If you have the 2002 Handbook they go into more detail right after 332.31, also they have a picture of the MI fittings.
332.31 adresses running the nuetral with the phase conductors.
332.31 Single Conductors.
Where single-conductor cables are used, all phase conductors and, where used, the neutral conductor shall be grouped together to minimize induced voltage on the sheath.