RTU disconect
laylasvegas
New member
do I have to mount a disconnect on a roof for a roof top unit. A buddy says I do not have to if the panel or panel room can be locked. I have ALWAYS installed a disconnect . Who is right??
440.14 Location
Disconnecting means shall be located within sight from and readily accessible from the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment.
The disconnecting means shall not be located on panels that are designed to allow access to the air-conditioning or refrigeration equipment.
Exception No. 1: Where the disconnecting means provided in accordance with 430.102(A) is capable of being locked in the open position, and the refrigerating or air-conditioning equipment is essential to an industrial process in a facility with written safety procedures, and where the conditions of maintenance and supervision ensure that only qualified persons service the equipment, a disconnecting means within sight from the equipment shall not be required. The provision for locking or adding a lock to the disconnecting means shall be permanently installed on or at the switch or circuit breaker used as the disconnecting means.
Exception No. 2: Where an attachment plug and receptacle serve as the disconnecting means in accordance with 440.13, their location shall be accessible but shall not be required to be readily accessible.
FPN: See Parts VII and IX of Article 430 for additional requirements.
I would venture to say that unless you meet one of the two exceptions noted that the disconnect has to be at or "within sight" (art. 100) and readily accessible (art. 100)
Pete
p.s. welcome to the forum:)