RTU feed size

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
The panel schedule, mechanical schedule and disco size for RTU-1 don't seem to makes sense based on unit being 10HP. The panel schedule is really screwed up as it says 1 phase leg...lol

Any thoughts? Thanks.
 

Attachments

  • Capture.jpg
    Capture.jpg
    19.9 KB · Views: 0
  • Capture 2.jpg
    Capture 2.jpg
    18.5 KB · Views: 0

jimdavis

Senior Member
The data in the images you posted is too small to read. From what I can make out, the supply fan in the RTU is 10 HP. The unit has a MCA of 97 amps, leading me to believe there is also a refrigeration package in it- compressor and condenser fan(s). Perhaps you can Google the Johnson Controls model number and get further information.
 

MyCleveland

Senior Member
Location
Cleveland, Ohio
If you are bidding, make the engineer or designer clarify (RFI).
Not your job, you will be pricing based on information, even though it may be correct, that your competitors do not have.
 