I have an RTU that doesn't have a duct smoke shut down input, it's old. The hvac guys have a third party controller added onto it. It won't allow an immediate shutdown upon alarm, it first goes through its purge cycle of a minute if we just break the t-stat.
Obviously not a desirable condition, and the HVAC company has finished this retrofit and will not play nice, their managers answer was 'how often do you really think are they going to have a fire?'.
So I've made the executive decision with the GC's blessing to break the 24 VAC powering the RTU's internal control board. It shuts down immediately, then powers right back up and restores normal operation when the duct smoke is reset.
I see no code compliance issues, might piss of the hvac guys, but they don't really care. Anyone think this noncompliant? (FD doesn't care either long as it shuts down)
Obviously not a desirable condition, and the HVAC company has finished this retrofit and will not play nice, their managers answer was 'how often do you really think are they going to have a fire?'.
So I've made the executive decision with the GC's blessing to break the 24 VAC powering the RTU's internal control board. It shuts down immediately, then powers right back up and restores normal operation when the duct smoke is reset.
I see no code compliance issues, might piss of the hvac guys, but they don't really care. Anyone think this noncompliant? (FD doesn't care either long as it shuts down)