I have the following RTU all 480V three phase with following MCA, breaker size protecting it, distance from breaker to RTU:
RTU 1: MCA: 46A, breaker size: 60A, distance: 150 feet
RTU 13: MCA: 48A, breaker size: 60A, distance:100 feet
RTU 14: MCA: 48A, breaker size 60A, distance: 70 feet
RTU 16: MCA: 50A, breaker size: 60A, distance: 80 feet
RTU 24: MCA: 49A, breaker size: 60A, distance : 60 feet
My question is for each of the RTU wire size should it be #6 AWG or #8 AWG? Assuming voltage drop less than 3%.