RTUs and cable sizing

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have the following RTU all 480V three phase with following MCA, breaker size protecting it, distance from breaker to RTU:

RTU 1: MCA: 46A, breaker size: 60A, distance: 150 feet

RTU 13: MCA: 48A, breaker size: 60A, distance:100 feet

RTU 14: MCA: 48A, breaker size 60A, distance: 70 feet

RTU 16: MCA: 50A, breaker size: 60A, distance: 80 feet

RTU 24: MCA: 49A, breaker size: 60A, distance : 60 feet

My question is for each of the RTU wire size should it be #6 AWG or #8 AWG? Assuming voltage drop less than 3%.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Your conductors can be #8 in all of these (assuming all terminations are rated 75 degree which is likely) as the conductors only need ampacity of the MCA not the breaker size.
 
Your conductors can be #8 in all of these (assuming all terminations are rated 75 degree which is likely) as the conductors only need ampacity of the MCA not the breaker size.

Actually it’s #6. #8 THHN is only rated for 45A now. You may be using too old of a code book.


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Actually it’s #6. #8 THHN is only rated for 45A now. You may be using too old of a code book.


Sent from my iPhone using Tapatalk
Curious, what Code cycle are you quoting. Still 50 amps in '17
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
Are you using NM somewhere along the circuit? Are the local jurisdictions adding restrictions?
 