Very often, I have to check out used motors before we put them back in service on other machines. I meg them, check bearings and end play, power them up and check the amps with no load.
Is there a "rule of thumb" that the motor amps should be on a no-load motor compared to the FLA?
Example: Today I had a 5 HP 460v motor with a FLA of 6.9 amps it was drawing 3.5 amps with no load, only a pulley on it. Megged good, bearings seemed OK. Installed it on a compressor and it blew a fuse instantly on start-up, compressor spins freely. Megged again at the starter to eliminate a bad wire, checked out OK, replaced the fuse, blew the same leg, 10 amp fuse, double element, slow blow fuse. Unhooked the wires pulled in the starter and the Voltage was 470 phase to phase, 271 to ground on all three legs.
Is there a "rule of thumb" that the motor amps should be on a no-load motor compared to the FLA?
Example: Today I had a 5 HP 460v motor with a FLA of 6.9 amps it was drawing 3.5 amps with no load, only a pulley on it. Megged good, bearings seemed OK. Installed it on a compressor and it blew a fuse instantly on start-up, compressor spins freely. Megged again at the starter to eliminate a bad wire, checked out OK, replaced the fuse, blew the same leg, 10 amp fuse, double element, slow blow fuse. Unhooked the wires pulled in the starter and the Voltage was 470 phase to phase, 271 to ground on all three legs.