Rules For Breaker Box Location

Status
Not open for further replies.

HotWire100

New member
For a residential dwelling re-model I would like to move the location of the main electrical box (breaker box) from its current location which is in an astheticly poor location to a utility room which includes a cloths washer, dryer, and a deep freezer. What rules apply to the location of a breaker box. Does it need to be seperated from the Clothes washer by distance or a closet of its own? Can it be located directly above the washer?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
For a residential dwelling re-model I would like to move the location of the main electrical box (breaker box) from its current location which is in an astheticly poor location to a utility room which includes a cloths washer, dryer, and a deep freezer. What rules apply to the location of a breaker box. ?

numerous. some are NEC 110.26, 408.36 and 240.24

Does it need to be seperated from the Clothes washer by distance or a closet of its own? ?
not normally, see 110.26

Can it be located directly above the washer?

No. See 110.26
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If moving to another room you might want to check this too:

VI. Service Equipment ? Disconnecting Means
230.70 General.
Means shall be provided to disconnect all conductors in a building or other structure from the service-entrance conductors.
(A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (A)(2), and (A)(3).
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
 