Below are some rules for puck light installations. Please feel free to add your own comments or rules
SUBJECT: Puck Light Installation
120 Volt Puck lights are not permitted for permanent installations unless they are wired with conduit & boxes
120 volt puck lights are not permitted to be spliced or installed under permanently installed cabinets.
Low voltage (12 volt) puck light wiring must not be concealed; it must be in a raceway in the walls and ceiling: boxes are required above lights when wiring & lights are concealed
Puck lights installed with the wiring open or visible. Must use a class II transformer rated at not more than 100 VA
Transformers with a VA rating of 101 to 1000 VA are class I. Class I wiring is required to be in conduit & Boxes. The secondary circuit must be protected not to exceed 25 amps.
Transformers or power supplies with the backward RU marking of UL laboratories are not UL approved to be used as a separate component. This is intended to be a factory installed component.
Outside direct burial low voltage wiring is not approved for use inside of the building
Attention should be given to the ampacity of the wire selected. A 300 watt 12 volt transformer will produce 25 amperes of current.
Many Puck light assemblies are only approved for portable use. They must be approved for permanent use under cabinets
Transformers may not be hidden in soffets & walls
SUBJECT: Puck Light Installation
120 Volt Puck lights are not permitted for permanent installations unless they are wired with conduit & boxes
120 volt puck lights are not permitted to be spliced or installed under permanently installed cabinets.
Low voltage (12 volt) puck light wiring must not be concealed; it must be in a raceway in the walls and ceiling: boxes are required above lights when wiring & lights are concealed
Puck lights installed with the wiring open or visible. Must use a class II transformer rated at not more than 100 VA
Transformers with a VA rating of 101 to 1000 VA are class I. Class I wiring is required to be in conduit & Boxes. The secondary circuit must be protected not to exceed 25 amps.
Transformers or power supplies with the backward RU marking of UL laboratories are not UL approved to be used as a separate component. This is intended to be a factory installed component.
Outside direct burial low voltage wiring is not approved for use inside of the building
Attention should be given to the ampacity of the wire selected. A 300 watt 12 volt transformer will produce 25 amperes of current.
Many Puck light assemblies are only approved for portable use. They must be approved for permanent use under cabinets
Transformers may not be hidden in soffets & walls