mshields
Senior Member
- Location
- Boston, MA
I'm always looking for rules of thumb to allow one to conceptually design on the fly. I'll give you one of my of my favorites and look forward to your inputs with others.
At 480V Current is approximately 1.2 times the KVA.
At 208V Current is approximately 3 times the KVA
To get fault current if the impedance is assumed to be 5%, you merely multiply the FLA times 20. Since impedance is more often than not 5.75, the number you come up with using the rule of thumb is always a safe one.
At 480V Current is approximately 1.2 times the KVA.
At 208V Current is approximately 3 times the KVA
To get fault current if the impedance is assumed to be 5%, you merely multiply the FLA times 20. Since impedance is more often than not 5.75, the number you come up with using the rule of thumb is always a safe one.