Going from one building to another outside i have feeder that is overhead SER cable without conduit. Can one use SER cable overhead feeder without conduit outside?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It will need support such as a messenger cable as Larry states, See Art 396 for aerial cables with messenger.
 