That Man
Member
- Location
- California, United States
- Occupation
- Electrical Designer
I'm designing a lighting system. The power is 3 phase 480, but all the lights are 277V single phase. To allow for switching half of the lights off, I'm running two separate 3 phase circuits and alternating the wiring in the luminaires. with 6 phase conductors, 2 neutrals, and a ground, I was concerned about wire mis-identification and came up with a color coding scheme, but ultimately it proved impractical, so back to traditional brn x2 org x2 yel x2 gry x2 grn.
But I got to thinkin. Can I separate the phases? So for one set of lights:
run phase A from circuit 1, phase B from circuit 2, two neutrals and a ground.
Another set of lights:
run phase B from circuit 1, phase C from circuit 2, two neutrals and a ground.
The final set of lights:
run phase C from circuit 1, phase A from circuit 2, two neutrals and a ground.
This way I'll be running 5 conductors (4 current carrying) instead of 9 conductors (8 current carrying). Is there a prohibition against separating the phases like this?
But I got to thinkin. Can I separate the phases? So for one set of lights:
run phase A from circuit 1, phase B from circuit 2, two neutrals and a ground.
Another set of lights:
run phase B from circuit 1, phase C from circuit 2, two neutrals and a ground.
The final set of lights:
run phase C from circuit 1, phase A from circuit 2, two neutrals and a ground.
This way I'll be running 5 conductors (4 current carrying) instead of 9 conductors (8 current carrying). Is there a prohibition against separating the phases like this?