craff
Member
- Location
- Southern California
We have a exterior retrofit job where we are swapping out existing fixtures for new CF wallpacks. The existing fixtures are not installed to code, i.e. using the space between fixture and wall for make up. I want to install the new fixtures to code by connecting interior j-box to fixture mount with a 8" rigid chase nipple. However, it means additional parts/labor. The consultant seems to think we can sleeve MC through existing conduit in concrete wall. Didn't think this was compliant. Also in order to use MC, we would have to drill a hole for the MC fitting, thus violating the UL listing and warranty. Is this allowable by the NEC