For a project at an industrial site, it was suggested to me to route a medium voltage feeder in conduit along the side of a building instead of running it underground due to the difficulty trenching in the location would entail.
I thought this was feasible until I read 225.60 & 225.61. It does not seem that routing along sides of buildings or roofs are allowed as the required clearances would be violated. Any thoughts on this? I know there are 4.16KV feeders used for chillers and even data center distribution. How are those not in violation of these clearences? Is it because they are in conduit? Do the clearances only apply to conductors in free air?
I thought this was feasible until I read 225.60 & 225.61. It does not seem that routing along sides of buildings or roofs are allowed as the required clearances would be violated. Any thoughts on this? I know there are 4.16KV feeders used for chillers and even data center distribution. How are those not in violation of these clearences? Is it because they are in conduit? Do the clearances only apply to conductors in free air?