Running 277V. with 120V in the same conduit. OK?

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
How about emergency circuits with other circuits in the same conduit. OK? Thank you for your help.
 
700.10(b) requires the circuits to be separate but 700.10(b) 1-5 will allow otherwise. Please read and see if they apply to your installation.
from 2011 NEC
 