If you hook up only the neutral from any source to a lamp will it light?
No
Why?
Not a complete circuit.
This same thing applies to the interconnected neutrals from two or more sources.
When a connection is made from the running generator to the main panel, and the street power is still on, the main panel has two active neutrals connected to the same bar from two different systems.
No, you have one 'active' neutral and the other is just a conductor that does nothing.
They are most likely operating at different voltages, 118v from the generator and 124v from the street.
Imagine the generator is just a portable one drop it on the ground right beside an outlet powered from the utility service.
Do not connect it to any thing but go head and start it up.
Get out your meter.
Measure the generators output and find its running at 124 volts
Measure the voltage at the service supplied outlet and find it's running at 118 volts.
Now measure the voltage between the neutrals of the generator and the service neutral. You will find 0 volts.
Why 0 volts when one circuit is 118 and one is 124 volts?
Because there is no complete circuit to measure.
You are trying to measure between one conductor from two different sources.
Hook the meter from the 'hot' of one source and the neutral of the other source and you still have 0 volts.
If you actually try this with a typical digital meter you will get some readings but these will be erroneous due to the meters sensitivity.
The only time one source will effect the other is if you tried to connect both the neutrals and hots from both sources at the same time.
Having the neutrals tied together from two sources is the way the majority of generators are wired.
You can get a transfer switch that will switch the neutrals but that is only required in a few applications.
One last thought.
If you took you meter and placed one lead on a 9 volt battery and the other lead on a 1.5 volt battery would your meter find any voltage difference?