Does code say anything on running air lines to boxes?
The OP question is regarding stainless boxes.Not that I know of. But watch your conduit fill when pulling tubing into conduit. I actually had a Contract NASA inspector ask me what % fill I had calculated.
300.8 Installation of Conductors with Other Systems. Raceways or cable trays containing electrical conductors shall not contain any pipe, tube, or equal for steam, water, air, gas, drainage, or any service other than electrical.
Is there a code reference for pneumatics?
I have installed control panels which had regulated compressed air run to them to maintain a positive internal pressure with in them. THis was mainly to keep contaminents out of the enclosures.
I do not believe this applies to enclosures containing, e.g. only solenoid valves. The requirement states you cannot have solenoid valves in an enclosure that contains electrical control equipment, which solenoids are not.He's correct.
NFPA 79 11.2.2.2- Pipelines, tubing, or devices (e.g., solenoid valves) for handling air, gases or liquids shall not belocated in enclosures or compartments containing electrical control equipment.
Exception #1 Equipment for cooling electronic devices
Exception #2 Piplines, tubing, or devices that are an integral part of listed equipment and separated by a suitable barrier.
Doesn't specify stainless enclosures. It seems to refer to all enclosures.
I have installed control panels which had regulated compressed air run to them to maintain a positive internal pressure with in them. THis was mainly to keep contaminents out of the enclosures.
He's correct.
NFPA 79 11.2.2.2- Pipelines, tubing, or devices (e.g., solenoid valves) for handling air, gases or liquids shall not belocated in enclosures or compartments containing electrical control equipment.
Exception #1 Equipment for cooling electronic devices
Exception #2 Piplines, tubing, or devices that are an integral part of listed equipment and separated by a suitable barrier.
Doesn't specify stainless enclosures. It seems to refer to all enclosures.
I do not believe this applies to enclosures containing, e.g. only solenoid valves. The requirement states you cannot have solenoid valves in an enclosure that contains electrical control equipment, which solenoids are not.
3.3.23 Control Equipment. Operating elements, such as relays,
contactors, circuit breakers, switches, solenoids, brakes,
and similar types of components, intended to govern or perform
a given function in the operation, including measuring,
sensing, monitoring, protecting, and regulating of machinery.
I don't disagree with the definition... because the term defined is Control Equipment, not Electrical Control Equipment. Solenoid valves are electro-mechanical devices in that they operate utilizing electrical phenomena but functional control of the valve itself is mechanical. That is, for the issue at hand, solenoid valves do not control electric.Given this definition in NFPA79 I would say it is clear that a solenoid valve is control equipment if it controls something on the machine (like a cylinder). Purge or pressurization lines definitely not since they serve no role in operating the machine itself.
I don't disagree with the definition... because the term defined is Control Equipment, not Electrical Control Equipment. Solenoid valves are electro-mechanical devices in that they operate utilizing electrical phenomena but functional control of the valve itself is mechanical. That is, for the issue at hand, solenoid valves do not control electric.
I agree... but the converse is not true, which is my point: Not all control equipment is electrical control equipment.Electrical control equipment is still control equipment.