Is anyone aware of a code stating that it is acceptable, or unacceptable, to run air supply tubing inside a wireway along with 480VAC, 3-Phase wires? My concern is that the air tubing may contain moisture and if it were to break water could get on the wires.
I do not see anything that specifically allows or disallows this, articles 300 and 310. However, from a design standpoint what would cause the tubing to break? For lack of better terms, a trauma to the wireway that is sufficient to break the air tubing would almost certainly also do some damage to the conductors. If the air carried through the tubing is caustic enough to erode it than I would also believe it would attack the insulation of the wiring. Even without the tubing the wireway could be subject to developing condensation through normal heating and cooling associated with ambient conditions. With the proper wire and insulation intact that should not be an issue. The only question I would raise on code application is with the addition of the tubing, does the wireway have to be recalculated for fill? The tubing is not carrying current, and therefore not dissipating additional heat, unless it is carrying hot air, like me with the post. However, it is taking up open space in the conduit. Is this a none issue?
I hope some of the more experienced members with industrial background will join in on this one.
this has come up in a previous post> I asked mike holt and he said he felt 725.3 would allow it, but this was a low voltage application.
My first comment is the air tubing would may have to be listed, the same as wire or optical fiber.
300.8 Installation of Conductors with Other Systems.
Raceways or cable trays containing electric conductors shall not contain any pipe, tube, or equal for steam, water, air, gas, drainage, or any service other than electrical.
Is the wireway that is discussed here Articles 376, and 378, 2003 NEC?
If so I would say this is a listing issue. Is the air tubing listed to be run in a wireway? Is the wireway listed for use with this particular tubing and its application?
Looking a little further, and Wireways are defined in Article 100 as raceways.
Raceways - An enclosed channel of metal or nonmetallic materials designed EXPRESSLY for holding wires, cables, or busbars, with additional functions as permitted in this Code.
I cannot locate elsewhere in this Code where it would permit this type of installation. I say it is not permitted.
My pleasure, that rule has been in the NEC for about 5 code cycles.
CMP 3 was trying to settle the issue in a Proposal related to different systems in the same trench, which is or may be covered in mechanical and plumbing codes, and 300.8 is the result of their actions.