I do not see anything that specifically allows or disallows this, articles 300 and 310. However, from a design standpoint what would cause the tubing to break? For lack of better terms, a trauma to the wireway that is sufficient to break the air tubing would almost certainly also do some damage to the conductors. If the air carried through the tubing is caustic enough to erode it than I would also believe it would attack the insulation of the wiring. Even without the tubing the wireway could be subject to developing condensation through normal heating and cooling associated with ambient conditions. With the proper wire and insulation intact that should not be an issue. The only question I would raise on code application is with the addition of the tubing, does the wireway have to be recalculated for fill? The tubing is not carrying current, and therefore not dissipating additional heat, unless it is carrying hot air, like me with the post. However, it is taking up open space in the conduit. Is this a none issue?