What would yo do. Obviously I choose to use a running board.

How bad is not that bad?Originally posted by aelectricalman:
.... Just use what the plumbers use, and drill a couple of 2 inch holes spaced out a bit and its not that bad.
That would be a 300.4(D) violation.We use them when running across a ceiling that will be rocked
Check:Originally posted by hurk27:
CelticThat would be a 300.4(D) violation.We use them when running across a ceiling that will be rocked![]()
334.15 Exposed Work. In exposed work, except as provided in 300.11(A), the cable shall be installed as specified in 334.15(A) through (C).
Regardless of whether the ceiling is getting finished or not, 334.15(C) allows 6/3 to be run under the joists.Originally posted by mc5w:
If I am going across a ceiling that I know will never be finished ( say 4 feet high ) and the cable is 6/3 then I do not need a running board.