With a "loose" interpretation of the requirement, yes. Under a "strict" interpretation, that would be non-compliant, especially if using an easily undone splicing means such as wire nutting. I think the intent of the requirement is so one can make or break all splices outside the opening when the box is small.
2008 ROP:
3-76 Log #1340 NEC-P03
Final Action: Reject
(300.14)
____________________________________________________________
Submitter:
Mike Holt, Mike Holt Enterprises
Recommendation:
Add the word ?unspliced?
300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points.
At least 150 mm (6 in.) of free
, unspliced,
conductor, measured from the
point in the box where it emerges from its raceway or cable sheath, shall be
left at each outlet, junction, and switch point for splices or the connection of
luminaires (fixtures) or devices. Where the opening to an outlet, junction, or
switch point is less than 200 mm (8 in.) in any dimension, each conductor shall
be long enough to extend at least 75 mm (3 in.) outside the opening.
Substantiation:
This change is to clarify that the free length of conductor is
required to be unspliced. As written, the code is vague as to whether or not the
conductor is permitted to contain a splice in the free length aforementioned.
Panel Meeting Action: Reject
Panel Statement:
The purpose of Section 300.14 is to permit access to the
end of the conductor. Whether this conductor is spliced or un-spliced does not
affect the length of this free end of the conductor. Many conductors originate
inside the box and are spliced to other conductors within the box but extend out
of the box for connection to a device of some kind. Making this change would
not permit this very common application. Even the exception to this section
states that unspliced or unterminated conductors do not have to comply with
300.14.
Number Eligible to Vote: 13
Ballot Results:
Affirmative: 13