Can this be done? It must be in 230 somewhere.:?
Or if there is a disco. one building #1 for building #2 can you run the feeders through building #1? The buildings are detached.Can this be done? It must be in 230 somewhere.:?
Can this be done? It must be in 230 somewhere.:?
230.3 One Building or Other Structure Not to Be Supplied
Through Another. Service conductors supplying a building or
other structure shall not pass through the interior of another
building or other structure.
230.6 Conductors Considered Outside the Building. Conductors
shall be considered outside of a building or other structure
under any of the following conditions:
(1) Where installed under not less than 50 mm (2 in.) of
concrete beneath a building or other structure
(2) Where installed within a building or other structure in a
raceway that is encased in concrete or brick not less than
50 mm (2 in.) thick
(3) Where installed in any vault that meets the construction
requirements of Article 450, Part III
(4) Where installed in conduit and under not less than
450 mm (18 in.) of earth beneath a building or other
structure
(5) Where installed within rigid metal conduit (Type RMC)
or intermediate metal conduit (Type IMC) used to
accommodate the clearance requirements in 230.24 and
routed directly through an eave but not a wall of a building
Or if there is a disco. one building #1 for building #2 can you run the feeders through building #1? The buildings are detached.
Or if there is a disco. one building #1 for building #2 can you run the feeders through building #1? The buildings are detached.
Why poorly worded? The title alone maybe leads to some misunderstanding - the content is pretty clear though.Yes. And I would go further and say you can run service conductors into the first building, hit a disconnect "nearest the point of entry" (as interpreted by your AHJ), and run the feeder for the second building through the first building.
230.3 is poorly worded IMO.
What you can't do is bring service conductors into first building, then leave the building again (still as service conductors), even if both incoming and outgoing are "nearest point of entry" to go to another building.
I think maybe could use a little work but think it does basically state that a service conductor inside one building can not directly supply another building. Many first look at that and say duh, you can't run service conductors through a building without overcurrent protection near the entry. But as worded it also means you can't bring service conductors into the building, hit a disconnect near entry but at same time put double lugs on that disconnect and go back outside to feed a second structure.I guess it's the pass through part. It seems they mean enter and exit as service conductors the whole way, but it's ok to enter and terminate. Also seems 230.3 is Un necessary as its already prohibited by the nearest point of entry clause.
I think maybe could use a little work but think it does basically state that a service conductor inside one building can not directly supply another building. Many first look at that and say duh, you can't run service conductors through a building without overcurrent protection near the entry. But as worded it also means you can't bring service conductors into the building, hit a disconnect near entry but at same time put double lugs on that disconnect and go back outside to feed a second structure.
In a situation where you could supply two structures from one service drop/lateral (like a house and a garage) that could be tempting, but the splice, tap, or whatever you may call it would have to be outside the first building to comply with 230.3.
Yes, there is no service conductors entering building 1 that don't also leave the building, still as service conductors.So are we in agreement that we can come into a building with two sets of SEC, one hitting a MB service panel to supply that building, and the other hitting a disco and continuing through that buildi ng as a feeder to supply another building? I think so, but it comes down to what exactly "pass through" means.
NEC doesn't have a problem with a locked door. Tenants still need access to their overcurrent protection though, unless there is on site staff that can provide access when necessary.Of someone were to lock that door then the tenants would not have access to shut down the power and the fire department as well would have to look for the service disconnect even with proper labeling and signs it was going to be a paper work night mare having to get easements with the city blah blah.
Sent from my SM-G950U using Tapatalk
NEC doesn't have a problem with a locked door. Tenants still need access to their overcurrent protection though, unless there is on site staff that can provide access when necessary.
Seen many single occupant buildings where fire dept may have a hard time finding where service disconnect is, add smoke and fire and it gets even harder.
On most SF dwellings and small commercial applications that might work. Larger services all that does is destroy the meter but won't interrupt voltage to the service equipment. I even run into an occasional larger dwelling with CT metering from time to time. Electric heat/water heating is usually the biggest reason for needing that kind of capacity. 10-15 years ago electric heat cost less to operate then gas heat around here, now gas is less again, chances are the electric rate remains steady over the years with only minor changes, gas is what will take a sudden change, up or down.Do you really think fire Dept will waste time finding the disconnect? They'll just give a hard whack with their double pointed-fiber glass-handled axe at the service meter if poco doesn't show up in 5 min or less.![]()