Is it acceptable by NEC to run multiple small power or lighting wire (COPPER PVC- THHN ) circuits inside a metal trunk for a hospital.
Normal, emergency, critical will be running in separate trunk.
Please advice.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
never heard it called trunk before.
At the med facility where I did work, the IT guys called it "trunking" whereas the electricians called the same enclosure "raceway". In regard to the OP, 517.31 does not allow wiring from essential systesm to share the same raceway or trunk with other wiring.
 