K KBot9 Member Location NYC Occupation Contractor Yesterday at 1:43 PM #1 Can I run a 3inch RMC with compression connectors through an Oil tank room with no stops or slices and fire-seal the penetrations?
Can I run a 3inch RMC with compression connectors through an Oil tank room with no stops or slices and fire-seal the penetrations?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Yesterday at 1:49 PM #2 Is the room a classified area?
K KBot9 Member Location NYC Occupation Contractor Yesterday at 2:23 PM #3 No not a Class 1 area, sealed oil tank ,no vapors, ventilation fan.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Yesterday at 3:12 PM #4 KBot9 said: No not a Class 1 area, sealed oil tank ,no vapors, ventilation fan. Click to expand... Since is had no hazardous classification then run whatever you want through it based on the code for normal wiring methods.