Running pre-wired pump cable in cable tray...

Status
Not open for further replies.

rustydud

Member
Location
Wisconsin
Hello all,

I have a pump. It is either 460VAC, 3-phase or 120VAC, 1-phase.
The pump comes with a permanently affixed, pre-wired 20' cable. This cable is either STOW-A or SJTOW-A depending on the voltage.

I have been asked to run this pre-wired 20' cable directly from the pump to a control panel via cable tray.

For someone who is more familiar with the NEC than I am, is this acceptable?
I know that running flexible cord in cable tray is "normally" not acceptable...but in my case, the cable is directly tied to a motor, so is there an exception to the rule for this?

Thanks!
 
Unless the cable is specifically approved for use in cable tray (see marking on cable), you can only run it in a raceway in the cable tray. See Table 392(10) for compliant wiring methods.
 
I have to ask this. How do you run a cord into a raceway supported by a cable tray?

If the raceway is not a complete system end to end it is not a raceway, or is it?
 
I have to ask this. How do you run a cord into a raceway supported by a cable tray?

If the raceway is not a complete system end to end it is not a raceway, or is it?

The idea was this:
Motor cable -> cable tray -> control panel

However, as stated, this motor cable cannot be run in cable tray according to the NEC.

Thanks.
 
I have to ask this. How do you run a cord into a raceway supported by a cable tray?

If the raceway is not a complete system end to end it is not a raceway, or is it?
The raceway has to be a complete run. The cable tray only serves as a support system [in part] between equipment enclosures
 
If the cord is permanently attached to the motor, how do you get an end to end raceway?
Well... you don't. ;)

But I believe a cable gland connector is a generally accepted method. With the cable terminated to the motor in such manner, one can reasonably assume the cable is permitted to be run exposed... at least for a short distance, with the balance protected against physical damage, be it by a sleeve or a sleeve-raceway hybrid using a cable gland as the means of raceway termination on the motor end.
 
Well... you don't. ;)

But I believe a cable gland connector is a generally accepted method. With the cable terminated to the motor in such manner, one can reasonably assume the cable is permitted to be run exposed... at least for a short distance, with the balance protected against physical damage, be it by a sleeve or a sleeve-raceway hybrid using a cable gland as the means of raceway termination on the motor end.

Correct.

By the way:
Suppose I have a sheet-metal shop and want to construct my own raceway out of sheet-metal. Would be made smooth such that there is no chance of the cable being cut or otherwise damaged when it is run through.​
Is this sort of "home-brew" sheet-metal raceway permitted by the NEC?​
 
A sheet metal sheath for physical protection would be just fine.
Call it a raceway instead and you may find that it has to be listed, and you would need approved fittings to enter and leave it.

Sent from my XT1585 using Tapatalk
 
A sheet metal sheath for physical protection would be just fine.
Call it a raceway instead and you may find that it has to be listed, and you would need approved fittings to enter and leave it.

Sent from my XT1585 using Tapatalk

I agree. Making your own substructure to carry MC cable, NM cable, etc. is ok, you can't pull THHN/THWN, XHHW, etc. though it, those must be installed in NEC recognized raceways, wireways, etc.

Next thing for OP is the fact he has flexible cord - which generally can't be installed as permanent wiring through building finish components either.
 
I would just run it in plastic outdoors or EMT indoors. Use a threaded coupling and a cord grip to exit to the pump. Or go to carflex
out of the tray or other raceway to the pump. I often see short unsupported cable runs from raceway to motor. Not sure about the
codes on this etc but it's a very common practice.
 