Running PV and Battery Wires Together

Status
Not open for further replies.

LostPuppy

New User
Location
San Diego, CA
Occupation
Engineer
Hi all,

I know in 690.31 B) it states that PV system DC circuits shall not occupy the same raceway as other non-PV systems.

Does this include the battery conductors that are running to the same MPPT?

Thanks in advance!
 
I would say no, it does not include them. You can run circuits together if they are paralleled at their terminations. But it may be open to interpretation.
 