We're receiving a XP motor with PTCs rather than temperature switches. I asked for temperature switches but our partner in the EU did not accommodate.
The PTC seems like a thermistor and basically a analog signal. From what I can tell this is typically shielded, especially if it's run in the same conduit as the motor leads, see https://www.eng-tips.com/viewthread.cfm?qid=109074.
Is it acceptable to run a shielded 2 conductor cable in the same conduit as the motor conductors? Obviously the shield would only be grounded at one end. I'm assuming the shield would have to be trimmed back where the explosion proof seals are, so the wires can be separated and sealed.
It seems common to run PTCs intrinsically safe but that doesn't seem like an option in this case because it's embedded in the motor winding and very close to the high voltages therein. Maybe that's an argument for leaving it unshielded altogether...
Thanks,
The PTC seems like a thermistor and basically a analog signal. From what I can tell this is typically shielded, especially if it's run in the same conduit as the motor leads, see https://www.eng-tips.com/viewthread.cfm?qid=109074.
Is it acceptable to run a shielded 2 conductor cable in the same conduit as the motor conductors? Obviously the shield would only be grounded at one end. I'm assuming the shield would have to be trimmed back where the explosion proof seals are, so the wires can be separated and sealed.
It seems common to run PTCs intrinsically safe but that doesn't seem like an option in this case because it's embedded in the motor winding and very close to the high voltages therein. Maybe that's an argument for leaving it unshielded altogether...