Rural Meter Base Location
Denakay10
Oklahoma
Medical Field
Our service meter is located about 358 ft as the crow flies from our house. Our meter breaker/disconnect is located there also. It literally is located behind the second house to our West. We have 1.5 acre lots, so this meter cannot be seen from any point near my house or our fence line (located approximately 2/3 of depth of our lot.) AND, I’m not sure yet whether our line runs through our neighbors‘ yards on easements or if it actually comes in at a 90° turn at the alley. Does this violate ANY code? I’d like to get the service company to at least move the meter where it can be readily located.
ANY code? Good question. That is pretty broad. The POCO may change it for you at your expense or you may have to hire an EC, again at your expense.
One of the reasons the 2020 will be requiring disconnects on the house in the future. That again is up to local interpretation because our SED will still allow a remote disconnect someplace on the property.
Thank you for the quick response! My house is the only in neighborhood with such a huge distance, the other two that are not located on their house, it is located directly behind their house. Is there any issue if my line runs through my neighbors’ backyards?
I think there can be an issue if the neighbors want to make something of it. I have a friend who has a similar situation but it is the power company line running underground thru the middle of his property. Not sure he can do anything about it but I believe your neighbors could make you move it
Back in NJ some 25 years ago the 'official' property map for my house showed an easement-- the power line to the neighbor's house was above the corner of my detached garage. It's likely that any such encroachments are legally logged.
By any chance was your house the first one there and then parcels around it got sold off but utilities (at least this line to your house) were never touched?
One of my father in laws neighbors lived in what was a rural setting and is now in city limits. Time to settle the estate and get the house sold the kids find out there was never a legal easement thru the surrounding property to get to the house. The owners of the surrounding property were fine with giving it but the city was now involved. They got it settled but not without a good deal of tension and hot words at several council meetings.
Your probably not going to find out what type of issue it's going to be until a problem arises with your service wiring.
That's when you'll get to see how understanding your neighbors are or are not if it runs through their property.
Seeing as how this seems to be on your side of the meter,moving it could entail a very large expense.
I know If my service wasn't causing me any grief at this point, I'd put it on the very bottom of the list of things I needed to get done.
JAP>
JAP>
Or you might be fine until the neighbor decides to build an outbuilding, pool or other activity that required excavation and they find your line in their property. With no easement they sort of have no responsibility to fix it if they damage it as well as the right to demand you have it routed around their property even though they are the ones that want to disturb it.
Which is exactly what I think I just said.
JAP>
JAP>
You never really specified they were excavating and then found it to be in the way for whatever they were doing. If they find out it is there for some reason but have no plans to excavate they may not care, some might not even be aware there needs to be an easement. When it is in their way for something then there is a problem and if they are not nice they may give you little or no warning to do something about it.
I said the issue would arise when there was a problem with your service wiring.
If they cut into it while they were excavating you would more than likely have a problem with your service wiring.
If they find it and don't mess with it your power is still on so it's a non issue.
when it's in their way for something then there may be a problem.
If they are not nice they may give you little or no warning before they cut it out of the way, hence, you have a problem with your service wiring like I said.
c-mon K-wired,,,, read between the lines every now and then.
JAP>
In a somewhat related story...
We were contracted to build a PV system on the roof of a customer's house and we were deciding where to hang our PV equipment - the disco, AC combiner, and PV meter. The obvious choice was the external wall on the side of the garage immediately opposite his MDP that was in his garage, but we were told that we couldn't do that. It seems that there was an error when the land was surveyed for laying out this new subdivision, and the lots did not match the civil plats of the land. We couldn't hang our equipment on that wall because our customer's house encroached onto his neighbor's property by about 6 inches; he didn't own the exterior wall of his own house. On the "bright" side he did own the exterior wall of his neighbor's house on the other side.
Lawyers were involved, but I never heard how the issue was resolved, if it ever was.
JAP>
Well if it is in raceway, conductor fails and you can pull new conductors without excavating, you and/or your neighbor can possibly not know exactly where it is below ground;);)
In that case no one would really care where it was located underground.
JAP>