Rusted Panel and Nameplate
1stwave
Is there a code volation for a rusted panel or nameplate. The panel is rated nema 1 and should have been nema 3. You can not read the nameplate. This switchgear panel is over 20 years old.
Thanks
jerryb
Re: Rusted Panel and Nameplate
Do you really want to read the nameplate? If the panel is rusted what are the existing conditions of the overcurrent devices and bus bars?
hurk27
Yes NEC 2002
110.12(C)
C) Integrity of Electrical Equipment and Connections. Internal parts of electrical equipment, including busbars, wiring terminals, insulators, and other surfaces, shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners, abrasives, or corrosive residues. There shall be no damaged parts that may adversely affect safe operation or mechanical strength of the equipment such as parts that are broken; bent; cut; or deteriorated by corrosion , chemical action, or overheating.