RV Calculated Loads

Status
Not open for further replies.

starbright28

Senior Member
Location
Minnesota
We have a RV post mounted box. It contains a 50Amp receptacle and a 20A receptacle. How do you calculate the load to shown on a panelboard schedule for the 50Amp receptacle?

Thanks.
 
551.73 tells you to figure the pedestal at 9600va. It then gives you a table of demand factors to apply depending on the # of pedestals in the panel. These demand factors are minimum and sometimes underestimate the load present.

Jim T
 