At an RV site I want to set a 200 amp service how many sites can I hit off of that service. Can I load it up to 200 amps on the main or am I limited to 160 amps?
Here is what I was thinking of doing let me know if its OK
One line diagram
200 amp 30 circuit panel (weather proof)
3, 125-amp DP breakers each feeding 3- 50/30/20 rv peds with #1/0,#1/0,#1/0,#2 AL Conductors
Service Calculations
9600va x .55 demand factor = 5280va
5280 X 9 sites = 47520va
47520va / 240v = 198 amps
Branch Circuit Calc.
9600va x .8 demand factor = 7680va
7680va x 3 sites = 23,040va
23040va / 240v = 96 amps
96 A x 1.25 = 120 A fused at 125
OR
If I can only go to 160-amps on main service then I only get 7 sites spread out on 3 circuits??
Here is what I was thinking of doing let me know if its OK
One line diagram
200 amp 30 circuit panel (weather proof)
3, 125-amp DP breakers each feeding 3- 50/30/20 rv peds with #1/0,#1/0,#1/0,#2 AL Conductors
Service Calculations
9600va x .55 demand factor = 5280va
5280 X 9 sites = 47520va
47520va / 240v = 198 amps
Branch Circuit Calc.
9600va x .8 demand factor = 7680va
7680va x 3 sites = 23,040va
23040va / 240v = 96 amps
96 A x 1.25 = 120 A fused at 125
OR
If I can only go to 160-amps on main service then I only get 7 sites spread out on 3 circuits??