A friend of mine plugged his 30a 125v RV into a generator about 50' away, and the GFI's did not work.He put his circuit tester into the GFI and it read "Reverse Polarity". He has a short pigtail adapter that has a 30a 125v TL on one end and a 30a 125v receptacle on the other that is wired correctly. When the RV is plugged directly into house power it is ok. With the Trailer unplugged from the pigtail the pigtail also reads ok. It seems the problem presents itself when the Generator get a load on it. Could a floating neutal in the Generator make the GFI's not work and the tester to read Reverse Polarity?
 
A friend of mine plugged his 30a 125v RV into a generator about 50' away, and the GFI's did not work.He put his circuit tester into the GFI and it read "Reverse Polarity". He has a short pigtail adapter that has a 30a 125v TL on one end and a 30a 125v receptacle on the other that is wired correctly. When the RV is plugged directly into house power it is ok. With the Trailer unplugged from the pigtail the pigtail also reads ok. It seems the problem presents itself when the Generator get a load on it. Could a floating neutal in the Generator make the GFI's not work and the tester to read Reverse Polarity?

I have had a receptacle tester show reversed polarity when the outlet was not grounded.
I'm not sure what it has shown on an unbonded system. But I think that the neutral not being bonded in the genset is worth looking into.
 
A friend of mine plugged his 30a 125v RV into a generator about 50' away, and the GFI's did not work.He put his circuit tester into the GFI and it read "Reverse Polarity". He has a short pigtail adapter that has a 30a 125v TL on one end and a 30a 125v receptacle on the other that is wired correctly. When the RV is plugged directly into house power it is ok. With the Trailer unplugged from the pigtail the pigtail also reads ok. It seems the problem presents itself when the Generator get a load on it. Could a floating neutal in the Generator make the GFI's not work and the tester to read Reverse Polarity?

Is the RV panel Neutral bonded? The neutral on the generator is most likely bonded. When you plug in the RV, it will trip the GFCI when a load is applied.
 
Many small portable generators do not have a neutral to equipment ground bond. There is no place for test current to flow when using one of those plug in testers because of this.

There is also no ground reference so if you should contact one of the system conductors there is no potential to anything else and you will not get shocked. Once there is a ground condition on one of the system conductors then you have a grounded system (even though unintended) a second fault at this point will allow for operation of overcurrent devices, and GFCI's.
 
I'd have to see a drawing of this to get my mind wrapped around it.
The receptacles on the generator are not GFI protected, it's an older unit.
If one were to install a jumper on the male end of the homemade pigtail between the Neutral and Ground Terminal for testing purposes, would it solve the issue?
 
I'd have to see a drawing of this to get my mind wrapped around it.
The receptacles on the generator are not GFI protected, it's an older unit.
If one were to install a jumper on the male end of the homemade pigtail between the Neutral and Ground Terminal for testing purposes, would it solve the issue?
It would make a path for the test current from the testing device to flow and allow the GFCI to trip when using this device to test. Not saying it is a good or bad idea to install this jumper otherwise.
 
Generator is defiantly not bonded as many older generators unbonded the neutral to ground bond when you switch the switch to use the 120/240 twist-loc receptacle, keep in mind that also with only a 120 volt load you are not going to get the full load from the generator as it is rated at the full 240 volt rating and with only using one side will give you only half of the generators output, the load if 120 volts will have to be split across both hots and neutral to get the full output from the generator but you can't do this with the twist-loc, we had several Colman's 5kw that had this switch and the neutral bond was lifted by the switch for using as a backup for a house, we found this out when we made a breakout box so we could have more receptacles and get the full rating of the generator from the twist loc instead of the two duplex receptacles on the generator when we checked the GFCIs in our breakout box, we just jumped the neutral to the ground in our twist-loc plug so we didn't modify the generator, I do remember some generators having a 30 amp RV receptacle that were made for RVs and if this is the case then I would expect that the neutral would be bonded? they also had the two 120 volt windings in the generator paralleled so it would produce the full output.

With the generator not running you can check for continuity between the ground and neutral at the twist-loc, or if the generator is running then using a loaded volt meter such as a wiggy or Ideal Volt-Con and check for 120 volts between a hot and EGC at the twist-loc
The test button on the GFCI should still trip which is the only UL accepted method for testing the GFCI's, GFCI's will still work without a ground if there is a path.
 
This generator has a 30a 125v TL Receptacle on it.

They made a short 2' pigtail that has a 30a TL male, to plug into this receptacle, and a 30a 125v RV Receptacle on the other end of the pigtail so they could plug the camper into it.
 