RV Panel
Yup
Canada
Campground supplies
1 - 120/240v 50amp
1 - 120v 30amp.
They used the 120/240 50amp feed for the building attached to the trailer, so all that is left is the 120v 30amp. The RV is 120/240, so we just dropped a hot and supplied the RV with 120v 30amp, essentially only running one leg of the RV panel for lights and plugs.
There are no 240v loads in the RV.
I am trying to think of a reason why this would be a bad idea?
is this a outbuilding supplied by a single branch circuit (one MWBC ) in accordance with 225.30 and the 250.32(a) exception applies, or is that building supplied by a feeder that serves more than one branch circuit in which case 250.32(a) as well as 225.30 both apply ??
It is a separate building built off the RV so we put a 50amp load center in there fed by the 120/240 50amp breaker supplied by campsite, it is a 12 cct load center, feeding lights, plugs and a small hvac.
So all that left them was the 120v 30amp to feed a 120/240v RV
Typically, the 50 to 30 amp adapter carried in the RV connects both legs of the panel to the single 120V line. Quite normal.
RVs don't have 240V loads. The ones that require 50A/240V have two HVAC units. But the HVAC units are 120V. The 240V is just so they have the ampacity to run both 120V units, plus the other 120V loads.