Trying to figure out a load calculation on a small rv park with 8 50 amp connects,and a 200 amp office/laundry and shower, 9600×8= 76800×.(.55)demand factor 42240 ÷240= 176 amps for the rv park plus a 200 amp main for the office, laundry and showers. I'd like to install a 400 amp main with 2 200 amp sub panels and branch each circuit off 1 200 amp panel , and install the other 200 amp main in the office. Any help would be greatly appreciated I am young struggling contractor. Thankyou in advance
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
If your under 2017 code the 9600va no longer applies, it has been changed to 12,000va for your site with 50 amp receptacle. BUMMER!

otherwise it looked like you had things figured out.
 