hi,
i went on a service call yesterday about lights flickering in a rv. Here's the situation: it's a small park (5, 30 amp 120 volt rv pedastals);they have 2 services. Both are 50' from transformer, one feeds the 5 rv pedastals and the other feeds the pump house; the lights flicker at both services. I checked all the connections, didn't find anything wrong, the voltage was 108 hot-ground 216 hot-hot at the panels. The owner has the power company coming out to check their side of the meter.has anybody come across anything like this before or have any ideas what would cause this problem??
Here's the second question, the service to the rv park comes into a meterbase with a 200 amp main breaker, then it feeds a 200 amp panel (they're mounted back to back on 6x6 pole with pvc conduit). In the panel there is no egc or gec and the neutral is isolated from the grounding bar. The neutral is bonded to the gec at the metermain, so I installed a egc from the metermain to the grounding bar in the panel. But now after reading 551.54 i'm having second thoughts on my installation - did I do it right or wrong. thanks for any insight.