Re: rv park service and wire to pedestal??
Originally posted by justwondering:
If i feed in and out (in a line)of say 10, 50 amp pedestals for 10 rv sites. I could run one 4/0 thhn set of conductors, right?
Looking at all of 551.73 that way of doing it looks acceptable. However I am not sure about your wire size. I am guessing you mean 4/0 aluminum?
10 sites 9600 VA = 400 amps
400 amps x .5 demand factor (Table 551.73) = 200 amps.
To me this is at least 3/0 copper or 250 aluminum you can not use the 90 C column.
4/0 AL is rated 180 amps @ 75 C you can not use 240.4(B) to round up to a 200 amp breaker because the the load is 200 amps.
I do not know if this load is considered continuous or not.
If it is continuous load the 10 sites would need to be on a 250 amp breaker which would move the conductors to at least 4/0 copper or 300 aluminum.
I did notice a FPN right under 551.73(C)
FPN:These demand factors may be inadequate in areas of extreme hot or cold temperature with loaded circuits for heating or air conditioning.
There is also this FPN under 551.73(D)
FPN
ue to the long circuit lengths typical in most recreational vehicle parks, feeder conductor sizes found in the ampacity tables of Article 310 may be inadequate to maintain the voltage regulation suggested in the fine print note to 210.19. Total circuit voltage drop is a sum of the voltage drops of each serial circuit segment, where the load for each segment is calculated using the load that segment sees and the demand factors of 551.73(A).
Not enforceable but something to think about.
It might be worth while to get an engineer involved with a project of this size and costs.
A service that looks to be 2500 Amps, 125 sites to feed 9600 VA to.
Did the power company stick with a 400 amp service recommendation? That is about 3 amps per site.
Good luck it sounds like it could be a nice job, Bob