hi i'm trying to design an addition to a existing rv park, here's the scope of the addition. this addition will be metered seperately from the rest of the park, 10 rv outlets modules ( meter , 20 amp 30 amp & 50 amp receptacles & breakers in each module) & a 15' x 15' bathroom with 50 gallon hot water tank,2 - 2k wall heaters acouple of receptacles & lights. on the outside of the bathroom is were the service will be installed. 6 rv sites on the right side & 4 rv sites on the left
my calc are
10 rv site = 96000 x 50% =48000/ 240= 200 amp
the bathrm is 46 amps
so i'll install a 320 meterbase & feed a 200 amp main breaker panel & a 200 amp disconnect.
the disconnect will feed 6 rv sites =144amp, & the panel will feed 4 rv sites= 120 amps and the bath rm at 46 amp for a total of 164 amps.
here are my questions
the feeders coming off the 200 amp disconnect sized for the calculated load, calculated load at 1.25% or the overcurrent protection.
i think its the calculated load at 1.25% which would be 180 amps & i can use 4/0 alum.
also i would like to use a 200 amp feed thru panel, to feed the other 4 rv sites would those feeders be sized 120 x 1.25= 150 amp or off the 200 amp main breaker
thanks for any help,i'm sure i'll have more questions,
my calc are
10 rv site = 96000 x 50% =48000/ 240= 200 amp
the bathrm is 46 amps
so i'll install a 320 meterbase & feed a 200 amp main breaker panel & a 200 amp disconnect.
the disconnect will feed 6 rv sites =144amp, & the panel will feed 4 rv sites= 120 amps and the bath rm at 46 amp for a total of 164 amps.
here are my questions
the feeders coming off the 200 amp disconnect sized for the calculated load, calculated load at 1.25% or the overcurrent protection.
i think its the calculated load at 1.25% which would be 180 amps & i can use 4/0 alum.
also i would like to use a 200 amp feed thru panel, to feed the other 4 rv sites would those feeders be sized 120 x 1.25= 150 amp or off the 200 amp main breaker
thanks for any help,i'm sure i'll have more questions,